What is the allowable ampacity for twenty 10 AWG THWN aluminum conductors in the same conduit at 30°C?

Prepare for the Electrical Code Calculations Test. Study with flashcards and multiple choice questions, each question has hints and explanations. Get ready for your exam!

To determine the allowable ampacity for twenty 10 AWG THWN aluminum conductors in the same conduit at 30°C, we start with the ampacity values from the NEC (National Electrical Code) table. For 10 AWG THWN aluminum conductors, the standard ampacity in a typical installation is around 30 amps at 30°C. However, when multiple conductors are placed within the same conduit, we must consider the derating factors due to the increased heat buildup among the conductors.

According to NEC guidelines, when conducting a calculation for multiple conductors, the ampacity must be derated based on the number of conductors present:

  • For three to five conductors, the ampacity is reduced to 80%.

  • For six to ten conductors, it reduces to 70%.

  • For eleven to twenty conductors, which is our case, the derating factor applied is typically 50%.

Given the standard rating of 30 amps for a single 10 AWG aluminum conductor, applying the 50% derating factor results in an allowable ampacity of:

30 A x 0.50 = 15 A

Thus, the allowable ampacity for twenty 10 AWG THWN aluminum conductors