For a noncontinuous load of 27 kW on a 3-phase, 480-volt circuit, determine the minimum standard size circuit breaker required.

Prepare for the Electrical Code Calculations Test. Study with flashcards and multiple choice questions, each question has hints and explanations. Get ready for your exam!

To determine the minimum standard size circuit breaker required for a noncontinuous load of 27 kW on a 3-phase, 480-volt circuit, you first need to calculate the full-load current (FLC). This is done using the formula for 3-phase power:

[

\text{Power (W)} = \sqrt{3} \times \text{Voltage (V)} \times \text{Current (A)}

]

Rearranging this to find the current gives:

[

\text{Current (A)} = \frac{\text{Power (W)}}{\sqrt{3} \times \text{Voltage (V)}}

]

Substituting the values:

[

\text{Current (A)} = \frac{27,000 , \text{W}}{\sqrt{3} \times 480 , \text{V}} \approx \frac{27,000}{830.3} \approx 32.5 , \text{A}

]

For noncontinuous loads, the NEC (National Electrical Code) allows you to size breakers at 125% of the calculated load current to ensure safety and account for potential inrush currents. Thus