Determine the ampacity for six 8 AWG THW copper conductors in EMT at an ambient temperature of 30°C.

Prepare for the Electrical Code Calculations Test. Study with flashcards and multiple choice questions, each question has hints and explanations. Get ready for your exam!

To determine the ampacity for six 8 AWG THW copper conductors in EMT at an ambient temperature of 30°C, it is essential to first refer to the National Electrical Code (NEC) tables that provide the standard ampacity for conductors based on their size, insulation type, and installation conditions.

For 8 AWG copper conductors, the base ampacity listed in Table 310.16 at 30°C is typically around 40 amps. This value is relevant for conductors that are installed under standard conditions without any derating factors considered, such as the number of conductors in a raceway or the ambient temperature being higher than 30°C.

However, when multiple conductors are installed together, like six 8 AWG conductors in an EMT conduit, you must apply a derating factor to account for the increased heat buildup among the conductors. According to NEC guidelines, six conductors would require a 10% derating. Thus, you would calculate the derated ampacity as follows:

  1. Start with the base ampacity for one conductor, which is 40 A.

  2. Apply the 10% derating: 40 A - (10% of 40 A) =